Here is something to consider for you guys. I am an electrical engineer and have installed more generation than I can count. First and foremost, save your selves some $$$ by sizing your genset correctly. Most homes will need no more than 15KW, but insure that the unit you choose has a 15KW continuous rating, with at least a 25KW peak rating. A 15 KW will run a 2400 sq ft house with no problem. this includes keeping the beer in the fridge cold, a freezer, AC, range, oven, lights, fans, and keep that boat battery charged in case the fish start biting. You might want to get the big one, but remember, its going to use more fuel. If you put in a 25KW and you only need 12.5, you are going to almost double your fuel use! Make sure you buy a revolving field generator and not a revolving armature. You get about 25% more efficiency. Insure that the unti has a skewed stator and displaced phase excitation so you won't fry the big screen and your air conditioning compressor starts easily without drawing the voltage down.
Next consideration is fuel. LP gas is the most reliable, natural gas may be shut down in an emergency. LP gas also provides a better heat rate, by 10% If you buy a 20KW and run it on LP, you get 20KW, run it on NG and it will only be good for 18KW. Doing the math (I won't bore you) a 15KW generator running at 1/2 load burns approximately 1.3 gals of propane an hour, or about 120 cu ft of NG. A 20KW (1/2 load) burns about 2 gals of LP, 225 of NG. A 25KW (1/2 load) burns about 3 gals of LP and about 275 cu ft of NG an hour. Another consideration is a 20 KW can be had as an air cooled unit, almost all 25KW are liquid cooled. Maintenance and $$$ consideration!!!
Other things to think about. Location, location, location! Put it on high ground, away from the house. They might be quiet, but they aren't that quiet. Make sure that you exercise your unit every month. You don't need to transfer power, but you do need to start it and run it for at least 30 minutes a month. Air cooled units are your best bet, water cooled have more maintenance. Make sure the genset is grounded and bonded to your utility power ground. Improperly grounded gensets can wreak havoc if the neutral floats.
Hope this helps.